How to wire T106 timer/ 240 volt/ SPDTApplies to T106R, T176, T106P3, T106M |
T106R / outdoor metal box/ 240 Volt 40 amp/ NO NC Buy T106R outdoor at Amazon Resources: T106R manual How to set and operate T100 series timers Sell sheet |
Larger image Day skipper T176 / indoor metal box/ 240 volt/ 40 amp/ NO NC terminals Buy T176 timer at Amazon Resources: T176R manual |
Larger image T106P3/ outdoor plastic box/ 240 Volt 40 amp/ NO NC Buy T106P3 beige plastic box T106R metal gray box |
Larger image T106M/ mechanism Buy T106M at Amazon |
Use only 600 volt wire. Lamp cord, extension cords are not rated 600 volt. Use copper wire only. Aluminum wire is fire risk and should be avoided or installed by professional. 30 amp breaker use 10 gauge / 120-240 volt 30 amp outlet can be installed on 30 amp breaker only/ use 10 gauge wire ... cannot be connected to 15-20-40 amp breaker. Orange/ #10 gauge wire, with ground ... 30 amp capacity. Safe maximum: 30 x 80% = 24 amps. Buy: 10-2 gauge/ 30 amp 10-3/ 30 amp Southwire electric tools |
Yellow
12 gauge 20 amp 120 volt 20 amp outlet can be installed on 20 amp breaker, but not 15 amp breaker/ use 12 ga wire. ... cannot be connected to 30-40 amp breaker. 1 Yellow/ #12 gauge wire, with ground ... 20 amp capacity. Safe maximum 16 amps. Buy: 12-2 gauge/ 20 amp 12-3/ 20 amp NMB is house wiring UF is underground Rolls of stranded wire HOOK UP Wires |
White
14 gauge 15 amp 120 volt 15 amp outlet, AFCI, GFCI, timer, switch etc can be installed on 15 or 20 amp breaker. Never connect 15 gauge wire to 20-30-40 amp breaker. White/ #14 gauge wire, with ground ... 15 amp capacity. Safe maximum 12 amps. Buy: 14-2 gauge/ 15 amp 14-3/ 15 amp NMB is house wiring UF is underground |
50-60
amp breaker use 6 gauge / 240 volt 50 outlet can be installed on 50 amp breaker only Buy: 6-2 wire Southwire electric tools NMB is house wiring UF is underground |
40-50
amp breaker use 8 gauge / 240 volt 40 amp outlet can be installed on 40 or 50 amp breaker only Buy: 8-2 wire Southwire electric tools NMB is house wiring UF is underground |
Copper ground wire. Every device, load, metal enclosure etc must be grounded. Ground wire must be continuous throughout installation, never switched on-off, never used as a Neutral wire. Generally ... use same size as other wire in circuit Buy: 12 gauge copper ground wire Ground wire Green ground wire Ground pigtails Ground rods/ ground clamps at Amazon |
Non metallic flexible cables must carry ground wire, but do not have hazard of short circuit causing injury from shock. Armored steel cable can be used as a grounded connection, and will protect wires from damage. Metal can be energized from an insulation failure. All conduit ...metal, plastic ... flexible and rigid ... must be attached to structure, and attached to enclosures, boxes. Movement, damage and deterioration are major cause of electrical failure. Buy: Non-metallic flexible conduit Power whip Armored cable Southwire armored cable cutter Pull boxes |
Electrical tools must be insulated. Always best to disconnect power, but insulation failure, lack of proper grounding, grounded neutral, lack of GFCI, out-of-code wiring, generator operating without transfer switch, and other problems still pose a risk to anyone working on electric power ... even when breaker is off. Buy: Electrician tools kits KLEIN TOOLS Tools kits IRWIN tools KNIPEX Telephone cable knife Low Voltage Mounting Bracket for Telephone |
600 volt 12 ga Stranded wire ot THHN wire is good for conduit with multiple wires ... but stranded cannot be installed under screw terminals on outlets, switches, timers etc without risk ... of heat causing splayed strands ....that come loose ... and begin to arc. Connect stranded to short piece of solid copper wire, and attach solid to screw terminal. Do not solder residential or commercial wiring. Project wire, extension cords, thermostat, bell and automotive wire are not rated for residential or commercial wiring. Only wire maked 600 volt can be used for permanent household wiring. Buy: Southwire 600 volt stranded wire Rolls of stranded wire HOOK UP Wires |
Protect wiring from damage Use nipper instead of pliers or screwdriver for removing staples (and nails). Do not damage cable or wires inside cable. -Code says: Cable SHALL BE secured without damage to the outer covering. NEC sec. 336-15 Buy End cutting nippers at Amazon |
Electrically insulated tools When removing insulation from wire, do NOT score or put cuts on surface of copper wire. Doing so increases resistance and heat on wire and creates possible weak point. Buy tools: KLEIN TOOLS Wire strippers at Amazon Electric Wire Stripping Machine Linesman pliers Utility knife at Amazon |
Multimeters Voltage is tested across two separate wires. Ohms or resistance is tested across both ends of same wire. Amperage is tested along one or two points on same wire. Buy: Analog multimeter Multimeters at Amazon Klein multimeter Electric testers at Amazon Clampmeter for testing amp flow on line |
GFCI circuit breaker A GFCI circuit breaker will protect all boxes on circuit. Circuit must be grounded. Ground wire must be continuous and connected to each piece of equipment. White wire on circuit breaker must be connected to Neutral busbar inside the breaker panel. Buy GFCI circuit breakers |
Push down 1" wide Push down breaker Plug-in breaker Buy single-pole: Choose from 15 to 60 amp Eaton CL series Siemens 15-60 amp Single-pole tandem breaker Tandem breakers |
Push down 2" wide Push down breaker Plug-in breakers Buy double-pole: Choose from 15 to 125 amp Choose from 15 amp to 200 amp Eaton CL series circuit breaker Siemens circuit breaker Double pole GFCI |
Wiring for T106 seriesDTSP/ single pull double throw timer: single activation of timer switch can turn on either high or low speed on pump |
|
Illustration from product manual
expanded to show complete wiring Buy: T106R outdoor timer Electrical tools must be insulated. Always best to disconnect power, but issues of insulation failure, lack of proper grounding, lack of GFCI, out-of-code wiring, generator operating without transfer switch, and other problems pose a risk to anyone working on electric power. Buy: Electrician tools kits Klein tools Tools kits |
|
>2-speed pool pump wire colors may be different than illustration >For example High speed might be White and Low speed Yellow Connect Low speed to NC terminals. High to NO terminal. |
T-106 timer: 2-speed 240 Volt pumpTimer acts as a high-low switch for continuous-running 2-speed pumps.T106 timer does not turn pump off. Use P1353 for 2-speed pumps that turn off >Or use 2 timers, and wire first timer before T106. Typically, a T104 timer would be integrated into circuit for that task. See wiring diagram for two timers Wire colors will be different. For example white wire may be Low speed. wiring diagram and instructions for pump Typically Low speed is running most of the time So connect Low speed wire to NC terminal 1, and High speed wire to NO terminal 4. Set timer to turn ON during times when High speed is needed. Minimum on-off is 1 hour. >Pump operates continuously. Install another timer on L2 Hot line to turn pump ON-OFF Pump motor must be grounded Resources: How to set Intermatic T100 series timers |
T-106 timer 277 volts/ Toggle between high and low speedT106 timer has NO NC terminalsWhen timer is OFF, then Pump receives power from 2 terminals ... terminal A and NC terminal 1 ... resulting in low speed. When timer is ON, then Pump receives power from 2 terminals ... terminal A and NO terminal 4 ... resulting in high speed. This means the Pump is always ON, so a second timer would be required to turn the Pump off at intermittent times. Typically, a T104 timer would be integrated into circuit for that task. Add Black tape to white wire that carries power Resources: How to set and operate T100 series timers T10604R manual T100 series parts Sell sheet T100 series timers/ all models shown |
|
Larger image T104 timer and T106 timer together Problem: The T106 timer is either high or low speed, but never OFF. The pump runs full time. To solve problem, a T104 is added to circuit. This means the T106 will toggle the pump between high and low speed. And the T104 timer turns off the pump. Note the T104 does not turn off the T106 timer ... instead it overrides the T106 and turns off the pump. When T104 timer turns off, the pump resumes high-low operation based on when the T106 timer is in high or low. Normally to accomplish this, the T10604R control center is used ... or you can buy the T106 and T104 separately Buy: T10604R with T106 and T104 together /208-240V for 2-speed pumps T104 series / buy T104R or T104P with outdoor box T104R metal outdoor box at Amazon T104P plastic outdoor box at Amazon T106R outdoor timer Resources: T10604 Door label Intermatic control centers plus manuals and parts |
|
T-106 timer 208-240 volts/ Toggle between 2 different loadsT106 timer has NO NC terminalsWhen timer is OFF, then NC Load 2 is ON, and NO Load 1 is OFF When timer is ON, the reverse happens, and Load 2 is OFF, and Load 1 is ON Use this configuration for 2-speed 240Volt pool pump that runs continuously. Use NO NC connections to change between High and Low speed For 120Volt application,.buy T105 timer. Or replace WG1573 clock motor with WG1570 Buy: WG1570 120 volt clock motor |
|
Resources See wire sizes and load ratings |
|
Resources: Other 40 Amp timers can control 2-speed pump: Intermatic GM40 GE 15207 Tork DTU40 Intermatic T1906 20 amp timer |
|
Larger image |
T106 and T104 timer control 2-speed pumpT104 turns pump on-off T106 changes pump from high speed to low speed Wire this configuration when 2-speed pump is not ON all the time Use T106 without T104 when 2-speed pump is ON all the timeBuy: T10604R with T106 and T104 /208-240V for 2-speed pumps Resources: T10604 Door label More control centers |
See P1353 manual and wiring |
2-speed alternative timerBuy:P1353 timer at Amazon PE153 at Amazon Resources: P1353 manuals and wiring For 2-speed pumps that do not run continuously, install P1353 timer. Snaps into any Intermatic enclosure |
Convert indoor timer into outdoor timer:Buy different enclosureBuy: 2T2502GA beige plastic Outdoor box at Amazon Resource Enclosures |
|
2-speed alternative timer/ 20 ampUse T1906 and T1975SPDT with NO NC terminals, For 2-speed pumps and other NO NC applications 15 minute time intervals instead of 1 hour for T106 T1976 has day skipper Resource: T1906 and T1976 wiring Lower amperage 120Volt timers with NO NC terminals:Resources:FM1 series PB series FMD series |
|
T-106 timer: Single-pole Normally ClosedThis lets you operate any 208-240 volt load using T106 timer.T106 acts like ordinary ON-OFF timer for any 208-240 volt load up to 40 amps. Normally Closed means the circuit is turned ON, and power is available to run Load. When timer activates, the circuit is turned OFF Move clock motor wires from A-3 to A-1 |
|
Larger image |
T-106 timer changes water heater temperatureUse timer for two different temperatures on electric water heater.Either upper thermostat andelement have power or lower thermostat and element have power. But not both at same time. Install ECO-protected thermostat for lower thermostat. Both upper and lower parts of tank are ECO-protected from overheating Rewire tank so upper and lower parts are separate. Use T106 timer to switch power between lower and upper parts of tank. Normal operation, the lower thermostat and element receive power and keep tank at temperature set point. Upper thermostat and element have no power. This is called 'redundant' water heater operation. This technique for heating tank more rapidly after cold water first enters tank. Resources: How to wire thermostats When timer activates, power to lower part of tank turns OFF. Power to upper part of tank begins. Upper thermostat is set for higher temperature. Since tank is at regular temperature, the higher setting means upper element will turn ON and begin heating tank to higher set point. Use this technique to heat water very hot for laundry cycle. Disadvantage: The lower part of tank will cool rapidly as new cold water enters tank, so this technique is good for making short-term batches of hot water. Resources: This technique applies to other timers: Intermatic GM40 timer Intermatic WHQ timer Tork DTU40 timer GE 15207 series timers |
T-106 clock motor 240 volt (208-277)Buy:WG1573 for 60 Hz 208-277V Amazon |
T106 timer clock motors>>>>> |
T-102 timer changed to 24 VoltsCW190-10 for 24 volt 60 Hz 24V at Intermatic |
|
T-106 changed to 120 VoltsBuy:WG1570 for 60 Hz 120V at Amazon |
Change T-106 changed to 60Hz to 50 HzWG1571-10D motor for 50 Hz 120VoltWG1574-10D motor for 50Hz 208-277V Amazon |
||
T-106 changed to 480 VoltsBuy:WG1576 for 60 Hz 480V at Amazon |
How to replace Intermatic clock motor | ||
TrippersDial can have 12 sets ON-OFF trippersBuy: 156T1978 trippers Amazon |
|||
Larger image |
InsulatorsTranslucent124T1952 double-pole T103, T104, T106 124T1952 double-pole T173, T174, T176 Buy: 124T1952 at Amazon 124T2411A black rigid |
||
Resource: How to take apart and repair T100 series timers |
Larger image |
Build your own 2 speed controllerAny Hp motor or pump40 amp relay & contactor = 5 Hp @ 240 voltBuy from my affiliate linksMagnecraft box and cover Magnecraft w199 relays Siemens power relays Schneider W199 relay NTE open frame relays Contactors/ reliable for heavy amp loads 15 amp Relays for loads up to 10 amps Resource: Difference between relay and contactor DC relays for solar panels Reverse motor using DPDT relay Control motor with 2 switches Start two motors at different times How to reverse motor with switch Relays for DC motors and solar panels Resources: How to assemble parts Compare programmable timers Wire size and amp charts for motors Information on contactors |
Wiring for other T100 series timers |
T101 Wiring: How to wire T101 and T171 series timers |
T101B Wiring: How to wire T101B timer Applies to T101B with separate wiring terminals |
T103 Wiring: How to wire T103 and T173 series timers |
T104 Wiring: How to wire T104 timer Applies to T103, T103R, T103P, T103M, T103PCD82, T173, T173R T173M see all models |
How to wire Intermatic T102: How to wire T102 and T172 series timers |
How to wire Intermatic
T105: How to wire T105 timer Nema 1 indoor enclosure/ To convert to 208-277V operation, replace WG1570 clock motor with WG1573 clock motor |
How to wire Intermatic T106
timer: How to wire T106 timer Nema 3R indoor-outdoor enclosure To convert to 120V operation, replace WG1573 clock motor with WG1570 clock motor |
How to wire Intermatic pool timer: How to wire pool timers |
Control centers: Control centers: + manuals and parts All control centers and parts |
|
Intermatic/ Grasslin enclosures Metal and plastic enclosures |
|
Intermatic sprinkler timers and wiring | How to wire Sprinkler timers + rain sensor + manuals + buying options How to connect rain sensor when timer does not have rain terminals How to Set & Troubleshoot Intermatic sprinkler timer/ pdf |
Multi-function timers and wiring 40 amp Multi function timers and manuals |
|
T1906-5 T1975-6 heavy duty timers 20 amp Multi function timers and manuals |
|
ET
series digital timers/ 20-30 amp/ 120-277 volt/ multi-channel
(same timer controls two circuits with different programming) ET series timers |
|
Timer modules/ 16 amp/ 12-240 volt Timer modules/ 16 amp/ 12 to 240 volt |
Buy
from my affiliate links every time/ thanks: Amazon As an Amazon Associate I earn from qualifying purchases Enter Amazon from any link on my site, fill cart with any item ... purchases pay small commission E-mail: geno03245w@gmail.com My response might end up in spam folder, check email folders Waterheatertimer on Twitter Message thru facebook |