How to wire T101 timer\40 amp for timer lights, motor, water heater, pump etc |
Large image Indoor metal box Buy: T101 series at Amazon Resources Sell sheet with model numbers Replacement clock motor T100 series repair parts How to operate and set T101 timer |
Larger image Indoor metal box/ day skipper Lets you skip one or more days per week Buy: T171 at Amazon |
Larger image Outdoor metal box Buy: T101R at Amazon |
Larger image Outdoor metal box/ day skipper Buy: T171R at Amazon T171RCR carry-over |
Larger image Mechanism only Use thumb spring located top inside timer to remove old mechanism from enclosure Buy: T101M at Amazon | Larger image Outdoor plastic box Buy: T101P at Amazon Outdoor plastic box/ see thru door Buy: T101PCD82 |
T101R3 Outdoor metal box Buy: T101R3 at Amazon |
T101R201 Outdoor metal box/ With fireman switch Buy: T101R201 at Amazon T101P201 Outdoor plastic box/ With fireman switch Buy: T101P201 at Amazon Resource: T101R201 manual Pool timers |
T-101
timer 120Volts Illustration from product manual Clock motor connects to Terminals A and 1 Resources: T101 series T171 skip-a-day series How to find Hot wire |
||||
T-101
timer 120Volts T-101 timer for 120 Volt water heaters T-101 SPST [single-pole single-throw] Black Hot wire must connect to pole 1. Neutral must go to pole A Black to Load goes to pole 2 White to Load goes to pole A |
||||
Larger image |
T-101 timer controls 3-phase Use T101 120Volt timer to control 3 phase loads. Same wiring diagram as above can control 3-pole contactor. Neutrals connect to terminal A Hot from breaker connects to terminal 1 Hot to contactor connects to terminal 2 No fuse required on incoming line. Fused disconnect required on 3-phase line and timer in most commercial applications Resource: 3-pole contactors |
|||
Larger image
T-101 timer controls any voltage/ single-phase or 3-phase The 2 and 3-pole contactors with 120 volt coil can be used to switch any voltage and amperage load on-off. This gives switching control for 208-240-277-347-480 volt,50-60-90 amp 3 phase or single phase loads. Buy contactor with 120 volt coil, and match the amp rating of contactor with the amp rating of load. Fused disconnect required on 3-phase line and timer in most commercial applications Resource: More 3-phase timers |
||||
|
T-101
timer 240 Volts Convert T101 into T102 timer to control 240Volt load: Replace 120volt WG1570 clock motor with WG1573 clock motor. Connect new clock to same terminals A and 1. 240V: L1 Hot from breaker connects to terminal A; L2 Hot from breaker connects to terminal 1 240Volt wires going to Load connect to terminals A and 2. T-101 changed to 240 V (207-277) Buy: WG1573 for 60 Hz 208-277V Amazon |
|||
|
||||
Override with switch Larger image |
Override
T100 series timer with 40 amp switch T100 series timers are rated 40 amp, 5 HP max Using a 40 amp motor control switch allows you to override any load that the timer successfully controls. Install switch inside any switch box. Watt or power consumption should appear on rating plate for each Load (motor, fan, lights, appliance etc) Divide watts by the voltage ... in this case, the voltage for T101 is 120 ... so if load consumes 3500 watts divided by 120 volt = 29 amps. This is within the 32 watt safe maximum of any 40 watt switch (safe maximum = 40 amps x 80% = 32 amps) Buy: 40 amp switch with 32 amp safe max Motor switch MS302 30 amp 2-pole switch Buy 30 amp switch with 24 amp safe max: 30 amp motor switch 30 amp 2-pole switch 30 amp industrial grade Leviton 3033 switch 30 amp 3-way switch |
|||
Larger image Override T101 using 40 amp contactor and freeze thermostat --A freeze thermostat or freeze switch will turn Load ON when temperature drops below 40°F, and then turn off when temperature rises again. -Low cost way to turn on pool or irrrigation pump or heater etc when freezing temperatures are expected. Note the contactor coil should be 120 volt, or same voltage as timer. -When temperatur drops, then the freeze thermostat completes circuit to the contactor coil. Contactor coil pulls the switching terminals together, and overrides the timer, turning on the Load. -Contactor is approx 2" wide, 2.3" long, and 2.6" tall. -There is generally NOT enough space in the wiring compartment of T101 to add a contactor. The contactor must be installed inside an electrically rated enclosure. Buy: Freeze thermostat Contactor 40 amp 120 Volt coil Packard contactor Mars 2-pole and 3-pole contactors Terminal kit Blue terminals for 16-14 wire Separate enclosure Resources: Enclosures Contactors and contactor wiring |
T101B
Wiring begins here Applies to T101B with separate wiring terminals |
|
T101B
timer / SPST / 40 amp/ 120V clock/ independent
switch terminals control
any voltage 120Volt clock motor Buy: T101B 120V SPST separate load terminals/ at Amazon Resources: T100 series sell sheet T101B manual/ pdf Note: You can accomplish same wiring using T104 timer & change clock motor You can accomplish same wiring using T103 timer |
Other timers and options | |
See P1353 manual and wiring |
Alternative timerBuy:P1353 timer at Amazon PE153 at Amazon Resources: P1353 manuals and wiring For 1 and 2-speed pumps that do not run continuously, install P1353 timer. Snaps into any Intermatic enclosure |
Convert indoor timer into outdoor timer:Buy different enclosureBuy: 2T2502GA beige plastic Outdoor box at Amazon Resource Enclosures |
Resources: Other 40 Amp timers can control 2-speed pump: Intermatic GM40 GE 15207 Tork DTU40 Intermatic T1906 20 amp timer |
Wiring Tips | |
Keep wires straight Use solid copper wire If wiring terminal or end of wire are covered with green, use emery board to clean terminal and sandpaper to clean wire. |
Larger image |
Both wires MUST be same gauge Straighten each wire If wire is corroded or overheated, clean the end with sandpaper and wipe with cloth. If wire has been melted, cut back and reattach, or replace wire. Tighten screw very tight against copper wire |
|
Use wire connector Use push-on wire connectors |
3 wires/
or different gauge wires Join wires with wire connector or push-on connector Run jumper to screw terminal. Buy: Red 3P connector (shown) for 10-14 gauge wire Lever connectors for stranded wire |
Fire safety/ Do not put stranded
wire under screw plate Do not install stranded wire under screw. Problem1: picture shows 2 different gauge wires under screw plate Problem2: Stranded wire will expand and contract and come loose under screw plate, even if it is the only wire under the screw plate Attach stranded wire and solid wire with wire connector, and run solid copper jumper wire to screw terminal Take photo of wires before starting. Resources: Timer caught fire Load ratings for Intermatic timers/ pdf |
||
Larger image |
Installation tips -Secure wire or conduit to enclosure. All wires, enclosures and conduit must be secured to structure. -Always use solid copper wire under timer screw terminals ... stranded wire can come loose and cause fires. -Keep enclosure door closed to prevent possible fire hazard from spreading. -Keep insulator over screw terminals to prevent accidental electrocution hazard. -Install enclosures away from hazards such as lawn mower or machinery. -Install outdoor boxes in sheltered area if possible and 12" above anticipated snowfall. -For safety, make sure Load is grounded correctly. People often forget to securely join the ground wires inside timer because wire sometimes gets a bit short. Buy extra length of wire from box store. Load must be grounded. Why you need ground wire |
12 Ga |
10 gauge or 12 gauge? Compare your wire with short pieces of 10 and 12 gauge wire from local box store 10 gauge for 30 amp breaker. 10 gauge wire can have black-white and sometimes black-red 12 gauge for 20 amp breaker 12 gauge will have black and white wires Buy: Southwire romex cable Resources: Match color code and amp rating for wire Basic house wiring |
Add black tape when White wire
carries voltage (applies to 208 and 240V circuits) With 120 and 277 Volt circuits, White wire is Neutral, and Black is Hot With 208 and 240 circuits, both wires are Hot, and both wires carry voltage Black tape on White wire identifies wire is Hot and not Neutral |
Use correct wire and breaker Oversized is OK, undersized is hazard Look at label on load to determind correct size wire and breaker Watts divided by volts = amps If Load is 120 volt, and watts is 1500 = 12.5 amps. Next calculate 80% safe maximum. 20 amp breaker x .80 = 16 amps safe maximum 15 amp breaker x .80 = 12 amps safe maximum The calculation shows that 4500 watt load requires 20 amp breaker and 12 gauge wire up to 150 feet. Longer distance, use larger wire and breaker. Buy from my affiliate links: Southwire cable and tools Resource: Figure volts amps watts |
Parts/ change voltage by changing clock motor | ||
Repairs etc Resources: Close up photos/ maintenance/ repairs Troubleshoot T100 series timer |
240 volt replacement Clock motors Buy: WG1573 208-277V WG1570 120V WG1576 480V CW190-10 for 24 volt 60 Hz 24V at Intermatic |
Trippers Up to 12 sets trippers can be put on dial Minimum 1 hour on-off Buy: 156T1978A T100 series trippers |
Larger image |
Insulators Translucent >124T1948 single pole T101, T102, T105 124T1948 single pole T171, T172, T175 >Buy: 124T1948 at Amazon Black rigid 124T2411A rigid Buy: At Amazon |
T-104 timer wired for 480
Volts Buy: WG1576 for 60 Hz 480V |
Change T104 timer by changing clock motor >>>>> Buy WG1573 replacement 240 volt for ordinary T104 240 volt clock motor |
T-104 timer changed into
T104-50 50 Hz timer for use in UK, India etc WG1574-10D motor 50Hz 208-277V Amazon T104-50 |
T-104 timer for 120 Volts Change T104 timer into 120 volt timer Buy: WG1570 for 60 Hz 120V Move clock motor wires to terminals A and 1 How to wire T103 |
How to replace Intermatic clock motor |
|
T-104 timer for 24 Volts CW190-10 for 24 volt 60 Hz 24V at Intermatic Move clock motor wires to terminals A and 1 |
Buy
T104 240 volt clock motor: WG1573 208-277V Amazon |
|
T101
Wiring: How to wire T101 and T171 series timers Applies to T101, T101R, T101P, T101PCD82, T171, T171R, T171CR, T101R3, T101P3, T101R201, T101P201, T101M, T171M see all models |
||
T101B
Wiring: How to wire T101B timer Applies to T101B with separate wiring terminals |
||
T103
Wiring: How to wire T103 timer Applies to T103, T103R, T103P, T103M, T103PCD82, T173, T173R T173M see all models |
||
How to wire Intermatic T102: How to wire T102 and T172 series timers | ||
How to
wire Intermatic T105: How to wire T105 timer Nema 1 indoor enclosure/ To convert to 208-277V operation, replace WG1570 clock motor with WG1573 clock motor |
||
How
to wire Intermatic T106 timer: How to wire T106 timer Nema 3R indoor-outdoor enclosure To convert to 120V operation, replace WG1573 clock motor with WG1570 clock motor |
||
How to wire Intermatic pool timer: How to wire pool timers |
More Intermatic timers | |
Control centers: Control centers: + manuals and parts All control centers and parts |
|
Intermatic/ Grasslin enclosures Metal and plastic enclosures |
|
Intermatic sprinkler timers and wiring
How to wire Sprinkler timers + rain sensor + manuals + buying options How to connect rain sensor when timer does not have rain terminals How to Set & Troubleshoot Intermatic sprinkler timer/ pdf |
|
\ Multi-function timers and wiring 40 amp Multi function timers and manuals |
|
T1906-5 T1975-6 heavy duty timers 20 amp Multi function timers and manuals |
|
ET series digital timers/ 20-30 amp/ 120-277 volt/ multi-channel (same timer controls two circuits with different programming) ET series timers |
|
Timer modules/ 16 amp/ 12-240 volt Timer modules/ 16 amp/ 12 to 240 volt |
Buy
from my affiliate links every time/ thanks: Amazon ''As an Amazon Associate I earn from qualifying purchases'' Enter Amazon from any link on my site, fill cart with any item ... purchases pay small commission E-mail: geno03245w@gmail.com My response might end up in spam folder, check email folders Waterheatertimer on Twitter Message thru facebook |