How
to wire T105 timer/ 40
amp/ 120 volt/ SPDT Applies to T105, T175 Resource: Safe electric wiring |
T105 / 240 Volt / NO NC Buy T105 at Amazon Resource T105 series models/ manuals |
T175/ With day skipper Buy T175 w/ day skipper Resource T175 series models/ manuals |
Use only 600 volt wire. Lamp cord, extension cords are not rated 600 volt. Use copper wire only. Aluminum wire is fire risk and should be avoided or installed by professional. 30 amp breaker use 10 gauge / 120-240 volt 30 amp outlet can be installed on 30 amp breaker only/ use 10 gauge wire ... cannot be connected to 15-20-40 amp breaker. Orange/ #10 gauge wire, with ground ... 30 amp capacity. Safe maximum: 30 x 80% = 24 amps. Buy: 10-2 gauge/ 30 amp 10-3/ 30 amp Southwire electric tools |
Yellow
12 gauge 20 amp 120 volt 20 amp outlet can be installed on 20 amp breaker, but not 15 amp breaker/ use 12 ga wire. ... cannot be connected to 30-40 amp breaker. 1 Yellow/ #12 gauge wire, with ground ... 20 amp capacity. Safe maximum 16 amps. Buy: 12-2 gauge/ 20 amp 12-3/ 20 amp NMB is house wiring UF is underground Rolls of stranded wire HOOK UP Wires |
Multimeters Voltage is tested across two separate wires. Ohms or resistance is tested across both ends of same wire. Amperage is tested along one or two points on same wire. Buy: Analog multimeter Multimeters at Amazon Klein multimeter Electric testers at Amazon Clampmeter for testing amp flow on line |
Electrical tools must be insulated. Always best to disconnect power, but insulation failure, lack of proper grounding, grounded neutral, lack of GFCI, out-of-code wiring, generator operating without transfer switch, and other problems still pose a risk to anyone working on electric power ... even when breaker is off. Buy: 1000 volt Tool kit Electrician tools kits KLEIN TOOLS Tools kits IRWIN tools KNIPEX Telephone cable knife Low Voltage Mounting Bracket for Telephone |
Protect wiring from damage Use nipper instead of pliers or screwdriver for removing staples (and nails). Do not damage cable or wires inside cable. -Code says: Cable SHALL BE secured without damage to the outer covering. NEC sec. 336-15 Buy End cutting nippers at Amazon |
Electrically insulated tools When removing insulation from wire, do NOT score or put cuts on surface of copper wire. Doing so increases resistance and heat on wire and creates possible weak point. Buy tools: KLEIN TOOLS Wire strippers at Amazon Electric Wire Stripping Machine Linesman pliers Utility knife at Amazon |
Weatherproof
lever switch on outdoor lights Safely operate outdoor toggle switch Replaces outdoor cover Install over top of ordinary switch Works with single-pole, double-pole, 3PST, 3-way, 4-way switches etc Use weatherproof box for outdoor Can be used indoor or outdoor Buy: Cantex lever switch Leviton lever switch Outdoor lever switches at Amazon Resource Cantex-toggle-switch-covers.pdf Cantex-PVC-junction-boxes.pdf |
Weatherproof wire connectorConnector cavity is full of siliconeBuilt-in cover keeps silicone in place Protect from water, dust etc Buy from my affiliate links Weatherproof size 14 to 6 Amazon Weatherproof size 22 to 8 Amazon Resource How to select and install connectors |
Multimeter Test for breaks in wire/ Test for voltage Most appliance require 80% rated voltage to function correctly Buy Analog multimeter Multimeters at Amazon Klein multimeter Electric testers at Amazon Clampmeter for testing amp flow on line Resource: How to test and replace element How to test thermocouple Element tests for 120 volts How to test wire |
Safety when testing wires: Never touch wet or previously flooded appliance. Never stand on wet surface when working on electric. Never stand on bare soil, put down dry boards. Tape tester leads to wood sticks to keep hands away from power. Use non-contact voltage tester before touching wires. Never touch or lean into any made of metal. Remove metal objects from pockets. Do not use oxygen or fuel accelerants in same room as electrical repairs Resource: Basic house wiring |
Weatherproof
outlet cover Safely use extension cord with weather resistant cover Buy: Outlet covers |
Weatherproof
box For adding outdoor wiring Drill through back of indoor box, and through wall to install new outdoor outlet. Buy Hubbell Bell PVC box Hubbell Bell aluminum box |
Wiring for T105 starts here120 volt |
|
Larger image |
Illustration
from product manual
expanded to show complete wiring Buy: T105 indoor timer Disconnect power Insulation failure, lack of proper grounding, lack of GFCI, out-of-code wiring, generator operating without transfer switch, and other problems pose a risk to anyone working on electric power. Buy: Electrician tools kits Klein tools Tools kits |
Larger image |
T-105 timer: 2-speed 120 Volt pumpTimer acts as a high-low switch for continuous-running 2-speed pumps.T105 timer does not turn pump off. Use P1353 for 2-speed pumps that turn off >Or use 2 timers, and wire first timer before T106. Typically, a T101 timer would be integrated into circuit for that task. Resources T105 manual T175 manual T100 series parts |
T-105 timer 120 volt/ Toggle between 2 different loadsT105 timer has NO NC terminalsWhen timer is OFF, then NC Load 2 is ON, and NO Load 1 is OFF When timer is ON, the reverse happens, and Load 2 is OFF, and Load 1 is ON Use this configuration for 2-speed 120Volt pool pump that runs continuously. Use NO NC connections to change between High and Low speed For 240Volt application,.buy T106 timer. Or replace WG1570 clock motor with WG1573 Buy: WG1573 240 volt clock motor |
Larger image |
T-105 timer: Single-pole Normally ClosedThis lets you operate any 120 volt load using T105 timer.T105 acts like ordinary ON-OFF timer for any 120 volt load up to 40 amps. Normally Closed means the circuit is turned ON, and power is available to run Load. When timer activates, the circuit is turned OFF Move clock motor wires from A-3 to A-1 |
Other timers and options | |
See P1353 manual and wiring |
2-speed alternative timerBuy:P1353 timer at Amazon PE153 at Amazon Resources: P1353 manuals and wiring For 2-speed pumps that do not run continuously, install P1353 timer. Snaps into any Intermatic enclosure |
Convert indoor timer into outdoor timer:Buy different enclosureBuy: 2T2502GA beige plastic Outdoor box at Amazon Resource Enclosures |
|
2-speed alternative timer/ 20 ampUse T1906 and T1975SPDT with NO NC terminals, For 2-speed pumps and other NO NC applications 15 minute time intervals instead of 1 hour for T106 T1976 has day skipper Resource: T1906 and T1976 wiring Lower amperage 120Volt timers with NO NC terminals:Resources:FM1 series PB series FMD series |
Resources: Other 40 Amp timers can control 2-speed pump: Intermatic GM40 GE 15207 Tork DTU40 Intermatic T1906 20 amp timer |
Wiring Tips | |
Keep wires straight Use solid copper wire If wiring terminal or end of wire are covered with green, use emery board to clean terminal and sandpaper to clean wire. |
Larger image |
Both wires MUST be same gauge Straighten each wire If wire is corroded or overheated, clean the end with sandpaper and wipe with cloth. If wire has been melted, cut back and reattach, or replace wire. Tighten screw very tight against copper wire |
|
Use wire connector Use push-on wire connectors |
3 wires/
or different gauge wires Join wires with wire connector or push-on connector Run jumper to screw terminal. Buy: Red 3P connector (shown) for 10-14 gauge wire Lever connectors for stranded wire |
Fire safety/ Do not put stranded
wire under screw plate Do not install stranded wire under screw. Problem1: picture shows 2 different gauge wires under screw plate Problem2: Stranded wire will expand and contract and come loose under screw plate, even if it is the only wire under the screw plate Attach stranded wire and solid wire with wire connector, and run solid copper jumper wire to screw terminal Take photo of wires before starting. Resources: Timer caught fire Load ratings for Intermatic timers/ pdf |
||
Larger image |
12 Ga |
10 gauge or 12 gauge? Compare your wire with short pieces of 10 and 12 gauge wire from local box store 10 gauge for 30 amp breaker. 10 gauge wire can have black-white and sometimes black-red 12 gauge for 20 amp breaker 12 gauge will have black and white wires Buy: Southwire romex cable Resources: Match color code and amp rating for wire Basic house wiring |
Add black tape when White wire
carries voltage (applies to 208 and 240V circuits) With 120 and 277 Volt circuits, White wire is Neutral, and Black is Hot With 208 and 240 circuits, both wires are Hot, and both wires carry voltage Black tape on White wire identifies wire is Hot and not Neutral |
Parts/ change voltage by changing clock motor | ||
Repairs etc Resources: Close up photos/ maintenance/ repairs Troubleshoot T100 series timer |
120 and 240 volt replacement Clock motors Buy: WG1573 208-277V WG1570 120V WG1576 480V CW190-10 for 24 volt 60 Hz 24V at Intermatic |
Trippers Up to 12 sets trippers can be put on dial Minimum 1 hour on-off Buy: 156T1978A T100 series trippers |
T-104 timer wired for 480
Volts Buy: WG1576 for 60 Hz 480V |
Change T104 timer by changing clock motor >>>>> Buy WG1573 replacement 240 volt for ordinary T104 240 volt clock motor |
T-104 timer changed into
T104-50 50 Hz timer for use in UK, India etc WG1574-10D motor 50Hz 208-277V Amazon T104-50 |
T-104 timer for 120 Volts Change T104 timer into 120 volt timer Buy: WG1570 for 60 Hz 120V Move clock motor wires to terminals A and 1 How to wire T103 |
How to replace Intermatic clock motor |
|
T-104 timer for 24 Volts CW190-10 for 24 volt 60 Hz 24V at Intermatic Move clock motor wires to terminals A and 1 |
Buy
T104 240 volt clock motor: WG1573 208-277V Amazon |
Larger image |
Insulators Translucent >124T1948 single pole T101, T102, T105 124T1948 single pole T171, T172, T175 >Buy: 124T1948 at Amazon Black rigid 124T2411A rigid Buy: At Amazon |
Wiring for other T100 series timers |
T101B Wiring: How to wire T101, T171 and T101B timer Applies to T101B with separate wiring terminals |
T103 Wiring: How to wire T103 and T173 series timers |
T104 Wiring: How to wire T104 timer Applies to T103, T103R, T103P, T103M, T103PCD82, T173, T173R T173M see all models |
How to wire Intermatic T102: How to wire T102 and T172 series timers |
How to wire Intermatic T106
timer: How to wire T106 timer Nema 3R indoor-outdoor enclosure To convert to 120V operation, replace WG1573 clock motor with WG1570 clock motor |
How to wire Intermatic pool timer: How to wire pool timers |
More Intermatic timers | |
Control centers: Control centers: + manuals and parts All control centers and parts |
|
Intermatic/ Grasslin enclosures Metal and plastic enclosures |
|
Intermatic sprinkler timers and wiring
How to wire Sprinkler timers + rain sensor + manuals + buying options How to connect rain sensor when timer does not have rain terminals How to Set & Troubleshoot Intermatic sprinkler timer/ pdf |
|
\ Multi-function timers and wiring 40 amp Multi function timers and manuals |
|
T1906-5 T1975-6 heavy duty timers 20 amp Multi function timers and manuals |
|
ET series digital timers/ 20-30 amp/ 120-277 volt/ multi-channel (same timer controls two circuits with different programming) ET series timers |
|
Timer modules/ 16 amp/ 12-240 volt Timer modules/ 16 amp/ 12 to 240 volt |
Buy
from my affiliate links every time/ thanks: Amazon ''As an Amazon Associate I earn from qualifying purchases'' Enter Amazon from any link on my site, fill cart with any item ... purchases pay small commission E-mail: geno03245w@gmail.com My response might end up in spam folder, check email folders Waterheatertimer on Twitter Message thru facebook |